salewis Mon 09 November 2009 04:33

Contactor for 115V...
 
I begin by saying that I'm nervous running 115vac out to the EPO switches that I am planning (one on gantry, one on table, probably one on control box) which is what the TECO CU-16-F6 from factorymation.com wants for the coil voltage..

What are the options (other than two-wire with braid for the 115vac)? Pros and cons?

jhiggins7 Mon 09 November 2009 21:01

I had the same concerns about running 115 volts out to the table unnecessarily. So, I used 12 volts for the E-Stop circuit. works fine and no need to run 115 volts to the table except for the router.

salewis Tue 10 November 2009 04:25

so then you have a 12V contactor then in the EPO (emergency power off) circuit?

I use EPO terminology rather than E-Stop to help remind myself that this is different than Mach3 E-Stop.

Stan

jhiggins7 Tue 10 November 2009 06:33

Stan,

Yes.

My design is described in this post including a schematic.