We used to mount the DIN (German Industry Standard) rails hard against the back panel, but then it was tricky to lay panel wires out the bottom of of one component and then to the top of the next component. Now we stand the DIN (Deutsche Industrie Norm) rail up on spacers so that we can pass the wires under the rail. Snag with this is that tracing the wires can lead to mistakes because they get hidden. (A dental mirror is useful for this tracing).
Here is a mix of top & bottom feed, even with the rail up on spacers. But I think that the flow is fairly logical. As you say, labelling and diagrams also help a lot. I just wanted your opinion if bottom feed might be against any codes? |
|
Hopefully the last question on the bottom/top issue: Would any laugh if I fed this contactor (as an example) from the bottom on the T1 T2 T3 terminals? I reckon that turning the contactor over for upside-down markings is a worse crime to commit.
|
As far as bottom feeding a contactor, I'm not sure. The only example I found was another Reliance Electric design, but they had relabeled the terminals. I found this short discussion also but I don't have the NEC handbook.
http://forums.mikeholt.com/archive/i...p/t-62360.html I also began to question the wisdom of switching the neutral. Again, there seems to be no definite rules against it I could find other than the mention below, and it may be referencing switching only the neutral. I don't remember it being something that is typically done in the US since the neutral is bonded to ground. http://www.isa.org/Template.cfm?Sect...ontentID=40708 |
On bottom feeding, thanks for finding that discussion, and let's just avoid it altogether. (I plan to make more graphical drawings of the components on the DIN rail and you have helped me tremendously with real industry feedback)
Switching of the neutral is something that Mike R also had big problems with, but he eventually relented when it was made clear that we only switch the neutral simultaneously with the Lives (Hots) on a single multipole switch or contactor. We never think of the Neutral as something that is connected to Ground (Earth). In fact, because we have lots of Ground Fault Protection, touching Neutral to Ground (Earth) causes a trip (fault). Look at all continental Europe 2-pin plugs for 230V - they can be inserted any way around. Snag is, we sometimes find that an idiot swops Neutral & Hot (Live) in a distribution board upstream and we are never 100% sure which of the two wires is 230V above ground potential. Maybe something similar to the US 230V single-phase where BOTH wires are treated with equal respect. Bottom line is that we prefer switching both wires, but only in a switch that forces them to be switched simultaneously. However, since I am going to end up producing circuits for the America's versus the non-America's, I can avoid neutral switching in the one case. |
Mike N, the simultaneous disconnecting of all Lives(Hots) and Neutral is equivalent to pulling the plug - what could be safer than that? :)
|
Quote:
The problem with breaking the neutral is that you don't know that it or the hot, really did break. Welded contacts are a fact of life. If you are holding a plug in your hand you can visually (or tactiley if you are vision impaired) tell that that all circuits are indeed disconnected. |
Quote:
|
Quote:
|
Mike your words have been very much appreciated. The readers keeping an eye on this thread must have noticed:
- how tricky this subject can get and some of the risks to be considered, - that it is not a simple DIY project to be tackled lightly - how unqualified I am to be the guide in this area |
Mike, how common is Ground Fault Protection over there? Would if be reasonable to specify that a MechMate can only be connected to a fused outlet with GFI? Out here that would be the de facto situation.
|
Quote:
As far as requiring GFI protection, it would certainly be a good idea. Considering the wiring is being done mostly by nonprofessionals and that wiring is in motion, it would be a small price to pay to avoid the potential shock hazard. Despite the best grounding efforts it would still be possible to have exposed wiring a person could come in contact with, without it necessarily grounding out. |
Installing a GFCI
|
1 Attachment(s)
I would like to offer this as a possible main power/E-Stop schematic. I am know the symbols are not standard, but I think you can get the idea. What we have is the a relay similar to what you have spec'd earlier except with a 24V control, and next to that is a 24V transformer. When the on button is press, the relay will transformer will turn on, energizing the relay, witch will then continue to feed the transformer after you have releaced the button. The benefits to this setup are, the power will remain off after a power outage, less high voltage wireing running through all the moving parts, and it also gives you a good source of power for iluminated switches.
|
Brian, 24V control is common in industrial electronics, but I am loathe to introduce yet another voltage into the control box - we have enough confusion in there already. The other benefits you mention are already present:
"The benefits to this setup are, the power will remain off after a power outage, less high voltage wireing running through all the moving parts, and it also gives you a good source of power for iluminated switches." Our latching circuit also stays off after a power outage and illuminated switches for 115V/230V are also easily available. |